Performance Approach
The fundamental reason for the creation of a
structure is placed at the forefront.
Innovation is permitted, even encouraged.
Characterization, measurement, and
prediction of performance are fundamental
concepts.
Performance approaches are not easy; therefore, in the short run, they are
not economical. In the long run, they can produce significant economies
through more appropriate allocation of resources.
Performance-Based Structural
Engineering
Historical review
Motivation
Communications
ICC Performance Code
Modern trends in
earthquake engineering
Performance levels
Global v local
evaluation
Primary and
secondary
Uncertainty
Performance Requirement
A qualitative statement
of a human need,
usually in the form of an
attribute that some
physical entity, process,
or person should
possess.
Prescriptive:
diameter bolts
spaced no more than 6
feet on center shall
anchor the wood sill of
an exterior wall to the
foundation.
Both types of rules are needed. Performance allows the better mousetrap.
Prescriptive allows economy to be reproduced. Continuing with rules for
conventional wood framed dwellings, the rules for double top plates,
minimum header sides, etc. Are all based upon normal spans and the
weakest available materials.
Why Prescriptive?
Simple to design and check.
Simple can be economical.
No need to re-invent the
wheel on every new project.
Our earthquake design standards have proven very vulnerable to the third
factor cited.
There are also instances in which the first item has been a real restraint:
many engineers designing dwellings of light wood framing strongly resisted
the change in the prescriptive assumption that all wood diaphragm structures
should be analyzed as flexible diaphragms, primarily because they were
comfortable with existing practice.
NBS Format
R
C
E
C
Consider floor surface. For housing, the old standard was a double wood
floor (rough board subfloor plus tongue and groove finish board); it was
being replaced by a single layer of plywood. How strong and stiff did it need
to be? NBS resorted to physical testing for the fundamental evaluation
procedure for innovating housing.
Three overall criteria, but only one has specific evaluation procedures. It is
the classic strength requirement in which strength is evaluated in a load and
resistance factor approach as shown partially in following slides.
Maximum Loads
U = 1.1 D + 1.45[Q + iFi]
where:
D = dead load
Q mean maximum variable load (= 1.25L, 1.2S,
1.0H, 0.85W, 1.4E, or 1.0T)
i = factor for arbitrary point in time load
Fi = L, S, H, W, E, or T
The concept that the maximum load effect from a set of variable loads can
be evaluated by taking one of the variable loads at its expected maximum
(the 1.45 times Q) plus the arbitrary point in time value for all the other
variable load, then repeating the exercise by rotating through the variable
loads, with each one being in the Q position once . . . this know as Turkstras
rule. It is much simpler than evaluating the total probability of joint
occurence of variable loads.
How safe is safe enough defined by either a probability of failure less than
0.001 per year or by a factored strength exceeding a factored load? The
probability is not computed directly in the factored load approach. Direct
computation of probability of failure in practice is difficult due to a lack of
statistical information. Probabilistic approaches are good tools for
consensus committees to evaluate the how safe question. When it is used
on an individual project, a peer review team is suggested.
Performance-based Design
Design specifically
intended to limit the
consequences of one or
more perils to defined
acceptable levels
Perils addressed:
wind, fire, snow,
earthquake, live loads
This could be rephrased as (1) protect public safety and health and (2)
provide functional serviceability. Of course there are other societal goals,
such as:
1. Controlling the economic impact of large scale natural disasters,
2. Reducing barriers to the disabled, and
3. Avoiding the uncontrolled release of toxic materials.
DING
BUIL
E
COD
Codes typically
prescribe design and
construction rules:
Believed capable of
attaining desired
performance
Largely based on
past poor
performance
BUILDIN
G
CODE
Performance-based Design
Requires the designer
to understand:
Intended
performance
Relationship
between design
features and
performance
Forces the designer to
predict expected
performance given
a design event
The understanding does not come easy. Our educational system for
structural engineers does not deliver it, and it is not developed naturally in
practice. Tools to predict performance, assuming significant inelastic
response in a dynamic event, are in their infancy.
Unacceptable
Earthquake Performance Level
Es
se
n
Ba
si
c
Ob
je
tia
ct
Sa
iv
lO
fe
e
ty
bj
ec
Cr
tiv
iti
ca
e
l
FEMA 356
Vision 2000
(new buildings)
FEMA 356
(existing buildings)
Vision 2000
A Framework for Performance
Based Structural Engineering
FEMA 350/351
(steel moment frame
buildings)
Vision 2000 was written by 1995. It set forth a form that recognized that
different levels of performance are necessary for different types of buildings,
especially where control of economic loss was necessary. The next step
was FEMA 273 for the rehabilitation of existing buildings; FEMA 356 is the
second edition of this document. The high expense of rehabilitation of
existing buildings drove a need for increased economy. The SAC project
developed a significant improvement in quantitative prediction of
performance.
Testing
Deemed to Comply
Construction
Performance =
Objective
Ground
Motion
x% - 50 years
Performance
Level
Performance Objectives
For performance-based design to be successful, the
needs of both the client and engineer must be
satisfied.
Engineer -Hazard must be
quantifiable and
performance must
be quantifiable
Performance Objectives
For performance-based design to be successful, both
the client and engineer must be satisfied
Hazard
0.30
0.20
Acceleration, g
0.10
0.00
-0.10
10
20
30
-0.20
-0.30
40
-0.40
-0.50
Time - Seconds
Hazard
Two methods of expression:
Deterministic
Magnitude x earthquake
on y fault
Probabilistic
x % probability of
exceedance in y years
for design event
Easy to understand
but . . .
there is considerable
uncertainty as to how
strong the motion from
such an event actually is.
Probability of Exceedance
Deterministic Hazards
1
0.9
0.8
0.7
0.6
0.5
0.4
0.3
0.2
0.1
0
0
0.2
0.4
0.6
0.8
1.2
1.4
1.2
1.4
0.12
0.1
0.08
0.06
0.04
0.02
0
-0.02
0.2
0.4
0.6
0.8
Probabilistic Hazards
Need to move clients to
probabilistic mind set.
Commonly used for other
considerations such as:
Probable occupancy rates,
Probable cost of
construction, and
Probable return on
investment.
Probabilistic Hazards
Low intensity shaking occurs frequently.
Moderate intensity shaking occurs occasionally.
Severe shaking occurs rarely.
Note that the curves on this chart are normalized to a design point at a 10%
probability of exceedance in 50 years. The significance is that the actual
peak ground acceleration at the design point is not 1.0g for any of the three
locations. It is accurate that the ground motions at more remote probabilities
are a larger multiple of the design point for Memphis than for San Francisco.
In fact the predicted ground motions in Memphis do exceed those for San
Francisco, but the annual frequency of occurrence at which this occurs is
between 0.001 and 0.0001.
Probabilistic Hazards
Probability of exceedance for design event:
10%/50 years
(500 year mean return) traditionally taken as
hazard for life safety protection
2%/50 years
(2,500 year mean return) traditionally taken as
hazard for collapse avoidance
Hazard for economic loss protection can be taken
at any level based on cost-benefit considerations.
Note that appropriately round numbers are used here for the mean return
interval. Engineers have a bad habit of going to extreme precision.
MRI
Frequency
50%-50 Year
72 Years
Frequent
20%-50 Year
225 Years
Occasional
Rare
Very Rare
2475 Years
The first, third, and fourth lines have been used or advocated for various
purposes. The 20% in 50 years has not been used much. Note the
unjustified precision in MRI, which is a direct computation based on the
Poisson assumption of earthquake occurrence.
Performance Level
The permissible amount
of damage, given that
design hazards are
experienced.
Engineers are not well trained to think of damage levels; our education
focuses on computation of specific strength limit states that are usually
idealized states (e.g., the plastic moment capacity of a steel beam or the
maximum bending moment capacity of a concrete beam) without much focus
on the formation of buckles in beam flanges or cracks in the concrete beam
let alone on how badly cracked a masonry faade will be when the structural
drift goes to a certain level.
The ICC Performance Code follows the tradition from the earlier work on
general structural performance. Much of it focuses on design for fire safety.
The following slides briefly review the general structure and the structural
performance criteria.
The concept is that societal needs change less rapidly than technological
solutions. Some recent trends, such as the Americans with Disabilities Act
and mandated energy conservation, belie that notion.
Procedures for verification are more important for innovative design. The
dots at the bottom indicate that there are more administrative functional
statements than shown here.
Risk factors:
Nature of hazard
Number of people
Length of time occupied
Sleep facility
Familiarity
Vulnerable groups
Relationships
Description
II
Normal buildings
III
Hazardous contents
IV
Essential facilities
Perf.
Group I
Severe
Perf.
Group II
Severe
Perf.
Group III
High
Perf.
Group IV
Mod
Severe
High
Mod
Mild
Medium
High
Mod
Mild
Mild
Small
Mod
Mild
Mild
Mild
(v.rare)
Large
(rare)
(frequent)
This damage level is close to the safety limit state for conventional
probabilistic load and resistance factor design.
Flood
Wind
Snow
Ice
Earthquake
20 100
50
25
25
25
Medium
50 500
75
30
50
72
Large
100 SS 100
50
100
475
V. large
500 SS 125
100
200
2475
Performance-Based Structural
Engineering
Historical review
Motivation
Communications
ICC Performance Code
Modern trends in
earthquake engineering
Performance levels
Global v local
evaluation
Primary and
secondary
Uncertainty
Repeat of the table of contents for this topic. The remainder of the
presentation will focus more specifically on earthquake engineering.
Performance-Based Earthquake
Engineering
Two driving factors:
High cost of upgrading existing structures
now considered unsafe
Requires more exacting assessment
High cost of damage and associated impacts
from structural performance in earthquakes
Higher performance criteria
Performance Levels
Engineer -amount of yielding,
buckling, cracking,
permanent deformation that
structure experiences
Standard Structural
Performance Levels
Joes
Operational
0%
Joes
Joes
Beer!
Food!
Beer!
Food!
Immediate
Occupancy
Beer!
Food!
Life
Safety
Damage or Loss
Collapse
Prevention
99%
These four categories are the currently favored standard levels; each will be
described in more detail.
Operational Level
Joes
Beer!
Food!
Joes
Beer!
Food!
Negligible structural
damage
Occupants safe during
event
Minor nonstructural
damage
Building is safe to
occupy but may not
function
Limited interruption of
operations
Losses < 15%
Joes
Beer!
Food!
Significant structural
damage
Some injuries may
occur
Extensive nonstructural
damage
Building not safe for
reoccupancy until
repaired
Losses < 30%
In conventional jargon, this is a yellow tag building. It is not a given that the
utilities would not function. The key issue here is that the structural safety,
or perhaps life safety provided by necessary nonstructural systems, is
compromised.
Joes
Loading Severity
Beer!
Food!
Beer!
Food!
Joes
Beer!
Food!
Structural Displacement
Evaluation Approach
4 - Determine
5 - Determine
drift & component performance
demands
Joes
10-1
10-2
10-3
Beer!
Food!
Lateral Force - V
1 - Select hazard
level
10-4
Joes
Beer!
Food!
LS
10-5
0
.5
1.0
1.5
2.0
2.5
CP
Lateral Displacement -
2 - Determine ground
motion Sa
3 - Run analysis
Note that this procedure does not address performance of external utilities,
which means that it cannot deliver any assurance of operational
performance.
Joes
Joes
Beer!
Food!
Beer!
Food!
If you want to limit structural performance to near linear behavior, then linear
analysis is adequate and economical.
Joes
Beer!
Food!
The great irony: Low budget structures are designed for more damage,
which, in reality, should require the most sophisticated, demanding, and
expensive engineering design. Dream on!
Judging Performance
Acceptability
Acceptance criteria are
indicators of whether
the predicted
performance is
adequate
Local (componentbased)
Global (overall
structure-based)
Nonstructural criteria can be added and are necessary for the higher
performance levels.
Force
Actuator
Deflection
Local (Component-based)
Acceptance Criteria
F
Life
Safety
Immediate
Occupancy
D
Collapse
Prevention
Brittle Behavior
(Force Controlled)
Ductile Behavior
(Deformation Controlled)
A key distinction is that components that exhibit brittle or near brittle behavior
are governed by strength requirements whereas ductile behavior is checked
on displacement/ductility (although force is a surrogate for displacement in
some methods).
Classification as a ductile component (or action) generally requires that
maximum displacement (without substantial loss of resistance) must exceed
twice the effective yield displacement.
The plot at the right shows a region of strength degradation; the vertical
transition is arbitrary and may need to be altered for analytical stability.
Collapse
Prevention
Building Configuration
Hierarchy of parts that comprise a building:
Elements
Components
Actions
Elements
Horizontal or vertical
subassemblies that
comprise a structure:
Braced frame
Moment frame
Shear wall
Diaphragm
Components
Individual members that
comprise an element:
Beam
Column
Joint
Brace
Pier
Footing
Damper
For shear walls, coupling beams, wall piers, etc, would be components.
Actions
Independent degrees of
freedom associated
with a component, each
with an associated force
and deformation:
Axial force elongation
Moment - rotation
Torsional moment twist
These are the most frequently used quantities for local acceptance criteria.
Secondary:
Any element
(component) {action}
that is not required to
provide the buildings
basic lateral
resistance.
May participate
but is not required
to do so.
This concept was developed in FEMA 273, driven by the need for realistic
and economical design of strengthening of deficient existing buildings.
Note that secondary elements do not have to be ductile; they may be brittle.
So long as their failure does not result in collapse of some portion of a
building (gravity load carrying capability) and the remaining elements
continue to provide adequate capacity for lateral loads, an element may be
considered secondary.
Plan
Perimeter walls
(Primary)
Elevation
Instructional Materials Complementing FEMA 451, Design Examples
Note that the slab-column frame is primary for gravity load but not for lateral
load.
Performance Evaluation
Primary Components
F
IO -
Immediate
occupancy
LS
CP
based on
appearance of
damage
CP - based on loss of
lateral load
resisting capacity
LS - 75 % CP
Life
safety
Collapse prevention
Instructional Materials Complementing FEMA 451, Design Examples
Performance Evaluation
Secondary Components
F
Immediate
occupancy
LS
CP
IO - based on
appearance of
damage
CP - based on
complete failure
of element
LS - 75% CP
Life
safety
Collapse prevention
Instructional Materials Complementing FEMA 451, Design Examples
Note that collapse prevention is essentially the loss of all capacity for
secondary components, which is a much larger displacement than allowed
for primary components.
Also note that immediate occupancy is unchanged from primary
components. For this performance level, the perception of damage is
important.
Collapse
Prevention
4- Find maximum
displacement
t
t
Global capacity
Maximum Displacement
Perception of a Guarantee
It was supposed
to provide
immediate occuancy!!
I followed the
guidelines???
Maybe I
should call
my
attorney!!!
0.5
0
0
0.1
0.2
0.3
0.4
16000
Capacity
uncertainty
Demand
Uncertainty
14000
12000
10000
8000
6000
4000
2000
0
0
10
20
30
40
The FEMA 273 approach appears relatively deterministic to the user, with
the exception that capacity reduction factors can vary with the degree of
knowledge about the resistance.
SAC extended the degree of consideration of variability in two significant
ways: factors to account for uncertainty in demand are explicitly selected,
depending on several parameters, and the confidence level of meeting a
criterion is computed.
Performance Objectives
Redefined
highly
I am moderately confident
not very
that there is less than x%
chance in 50 years
that damage will be worse than
Immediate occupancy
Collapse prevention
Instructional Materials Complementing FEMA 451, Design Examples
Within the integral is the probability that demand exceeds capacity given a
certain ground motion, to be integrated over the probability of occurrence of
the ground motion
Note that b is the slope of the demand vs ground motion relation at the level
of interest
More detail on following slides
Capacity
uncertainty
LATERAL RESISTANCE ( kips)
16000
14000
12000
10000
8000
6000
4000
CU
2000
0
0
10
20
30
40
For this example the capacity limit is taken at essentially the beginning of
nonlinear behavior, which happens to be the beginning of capacity
degradation for this system. Beta is a measure of the scatter about the
mean capacity limit
16000
Demand
Uncertainty
14000
12000
10000
8000
6000
4000
DU
2000
0
0
10
20
30
40
=e
k 2
DR
2b
; a = CB e
k 2
DU
2b
; = e
k 2
2
CU + CR
2b
aD
C
In the SAC approach two load factors (gammas) are used, along with one
resistance factor.
All factors depend on the ratio of two slopes: k being the slope of the hazard
curve, b being the slope of the demand vs ground motion level relation; both
evaluated at the design point (tangent, not secant)
Gamma depends on the variability inherent in the prediction of demand
(incorporates scatter in response of real structures to real ground motion)
Gamma-sub-a depends on the bias and variability introduced by structural
analysis, and varies with the method
Procedure
3. Correct predicted
maximum demands
for known inaccuracies
in prediction method
to obtain median estimate
of demand.
aD
In FEMA 350 gamma factors vary with the performance level, the type of
moment frame connection, and the height of the building, and gamma-sub-a
factors vary with these three factors plus the type of analysis procedure used
Procedure
( a D )
=
C
4. Compute factored
demand to capacity ratio
(DCR)
Confidence
2%
3.0
5%
2.6
10%
2.2
20%
1.9
30%
1.6
40%
1.5
50%
1.3
60%
1.2
70%
1.1
80%
0.95
90%
0.8
95%
0.7
98%
0.5
Capacities (C ) and resistance factors phi are specified for various types of
connection details.
The lambda values shown are approximate for an uncertainty level in
demand and capacity on the order of 30 to 40%
16000
Capacity
uncertainty
Demand
Uncertainty
14000
12000
10000
8000
6000
4000
2000
0
0
10
20
30
40
16000
Capacity
uncertainty
Demand
Uncertainty
14000
12000
10000
8000
6000
4000
2000
0
0
10
20
30
40
Very little overlap of demand and capacity. If the uncertainties were very
small, then the ratio of demand to capacity would only need to be slightly
less than 1.0 for high confidence. We have large amount of uncertainty,
therefore the ratio must be less than 1.0 for reasonable high confidence.
Summary
Performance-based design for earthquake resistance
is possible.
There is considerable uncertainty associated with
prediction of performance.
LRFD approach developed for steel moment frame
buildings allows the engineer to be honest as to
confidence that performance may (or may not) be
achieved.
Communication is more complex but less dangerous.
Extensive work necessary to derive demand and
resistance factors for various structural systems for
general application.
At this time, the approach for steel moment frames is relatively complex.
The profession certainly does not understand it well. Thus, further
development is appropriate, is underway, and changes should be expected.
The amount of work to develop the quantitative values for other systems will
be expensive and time consuming.