Topic3 Ventilation Part 2
Topic3 Ventilation Part 2
VENTILATION
Ventilation Systems
Natural ventilation cannot be relied upon to always
provide enough fresh air to meet requirements.
Also more control can be obtained by using fans to supply
air to a space or to remove contaminated air from a
space.
Some mechanical ventilation systems use fans for both
supplying and extracting air, thus mechanical ventilation
systems may be classified as follows:
1.
2.
3.
Supply system
Extract system
Balanced system.
i)
ii)
Introduction
EXHAUST SYSTEM
Mechanical Air Supply with Natural Air
Exhaust
Air supply is controlled mechanically and
the air exhaust takes place on a natural
way by ventilation openings, windows or
shafts. There will be an overpressure in the
building.
An air filter used to clean the incoming air.
A ventilator (or fan) controls the air supply
and the outdoor air is transported into the
building by ducts.
By controlling the ventilator it is possible to
control the ventilation capacity for the
system.
EXHAUST SYSTEM
Natural air supply with mechanical air exhaust
Popular form of ventilation in residential and offices.
The mechanical air exhaust system creates an under pressure in the building, the
system is less dependent on the weather. The under pressure creates a pressure
difference over the ventilation openings encourage the air to suck in.
Ventilation capacity (air out) controlled by an exhaust ventilator.
EXHAUST SYSTEM
1. Supply
Ventilation System
Spot exhaust fans are still needed in high-pollutant areas such as the
kitchen, bathroom, and laundry room.
A supply system slightly pressurizes the house by drawing outdoor air into the
house. This pressurization pushes indoor air out through small openings in the
building, which helps to prevent outside moisture and pollutants from getting in
through these passages. Positive indoor pressure also protects against back
drafting.
3.
Improved comfort.
Improved health.
SA = Supply air
RA = Return air
OA = Outside air
EA = Exhaust air
A typical fan
The centrifugal
type generally
supplies more
cfm per
horsepower at
static pressures
over 4.0-4.5
inches of water
and is often
used where low
noise level is
desired
The vane-axial type has a propeller and vanes, and is best for static pressures under 4.0-4.5 inches of water
ADVANTAGES OF GOOD
VENTILATION
1.0 REDUCTION IN HUMIDITY LEVELS
-Dust-mite levels decrease
-Mould disappears
-Fungus disappears
2.0 REMOVES THE CAUSE OF TIREDNESS AND HEADACHES
-High CO levels are replaced with fresh air
-Moist, stuffy air is eliminated
-Poisonous particles emitted by artificial building materials are removed
1. 1000 litres
2. 1 litre / sec
3. 1 litre/ sec
=
=
=
1 m3
3600 litres/ hour
3.6 m3/ hour
The volume of fresh air (make up air) required for proper ventilation is determined of the size and use of the space.
min 4
Assembly halls
4-6
12 - 15
Auditoriums
8 - 15
Bakeries
20 - 30
Banks
4 - 10
Barber Shops
6 - 10
Bars
20 - 30
Beauty Shops
6 - 10
Boiler rooms
15 - 20
Q=nV
(1)
where
EXAMPLE 1
QUESTION 1
A room 15m x 7m x 2.8m high is to have a ventilation
rate of have a ventilation rate of 11 air changes/ hour.
Calculate fresh air entering the room through ductwork
QUESTION 2
Air enters an office through a 250mm x 200mm duct at a
velocity of 5m/s. The room dimensions are 5m x 3m x 3m.
Calculate the room air change rate.
Solution:
Q = nV ---------- (1)
Where n = ? ; V = 5 x 3 x 3 = 45m3
A = Q/v --------------- (2)
Where A = cross area of ducting, 0.25 x 0.2 = 0.05m2
V = velocity of air = 5 m/s
0.05 = Q/5
Q = 0.25 m3/s
= Therefore , equation(1)
0.25m3/s = n(45)
EXERCISE
Answer
The air ow rate is given by:
Q = (N air changes/hour) (Vm3/air change) (1h/3600s)
where room volume Vm3 = 1 air change. Hence
Q = (NV/3600) m/s
= (11 15 7 2.8) / (3600) m3/s
= 0.9 m3/s
Also, Q
=AxV
Q m3/s = duct cross-sectional area A m2 air velocity V m/s
Therefore
A = Q/V = (0.9/8.5) m2 = 0.106 m2
EXERCISE
A retail shop 22.0m x 6.5m x 3.5m has 7.5 air changes/hour from
air supplied through a duct where it flows at a velocity of 9.5 m/s.
Calculate the air volume ow rate to the room and the dimensions
of the square duct.
The Male Toilet and Female Toilet should each have separate extract
ventilation systems to avoid cross-talk and spread of smoke within
the ductwork system.
36.45 m3
= 0.081 m3/s.
8 AC/h
0.081 / 4 =
0.02025 m2.
( 0.02025 )0.5