2023-TSO-UGM Topic4 MonitoringSystemForSubSynchronousOscillations
2023-TSO-UGM Topic4 MonitoringSystemForSubSynchronousOscillations
1. Background 4. Specification
• Power system description • Sensitivity
• NER • Triggers
• AEMO and NSP
5. Performance
2. Problem description • Field test monitor files
• Observed issues • Factory test
• Issues for TNSP and AEMO
• Regulatory requirements 6. Customisation
• Programmable back-end
3. Equipment overview • Multiple OSM base station
• Hardware • Additional functionality
• Architecture
• Connections
Includes:
Guidelines
• Market Rules
• Grid Code Procedures
• PS Operation
• Connections
• Tech standards
• Metering Codes
Network bodies
• Transmission Network Service Providers – TNSP
• Typically one per state, total of five
• Distribution Network Service Providers – DNSP
• Can be several per state, total is about eleven
• Longitudinal structure
• N-S is about – 2500 km
• W-E is about – 1600 km
• HVDC link to Tasmania – 300 km
• AEMO has observed intermittent lightly damped oscillations in parts of the system where:
• Many inverter-based generating system have been installed
• In parts of the transmission system that are weak – low fault level
There is a need to monitor generating systems (and the power system generally) to detect when these oscillations are
occurring.
This presentation discusses the development of such a monitoring system using:
• DIgSILENT Power Factory Monitor
• Grid Code software tools
◦ References:
− Map = AEMO
− Capacities = AER
◦ References:
− Map = AEMO
− Capacities = AER
• Intermittent oscillations in voltage have been observed at various locations where inverter-based generation is connected.
• Issue seems to be worse when power system is weak (low fault level)
• Oscillations are generally in the 5-25 Hz range
• Oscillations are fading, lightly damped and appear as limit cycles, as amplitude modulation of voltage
• Amplitudes of up to 4% have been observed but more commonly around 1% of transmission voltage.
• There is also a Technical Rule (S5.2.5.10) that requires unstable generators to trip / disconnect
• Originally intended for Synchronous machines (reverse power, out of step protection etc)
• Not clear for inverter-based generation
An objective is to develop, agree, implement and commission a suitable protection system that takes into
account nearby plant and their interaction/contribution (desired or undesired) to unstable operation [Aemo]
Australian National Electricity Market (NEM) has a requirement for unstable operation to be detected.
Some NSP requirements (verbal –formal guideline issued by only one NSP out of five)
• Do NOT trip if generating system is acting to reduce amplitude of oscillations
• Prefer site specific requirements
• 0.1 Hz at the lower end of frequency range
Main features:
• Modular data acquisition system
• Direct measurement from VT and CT
• Analog and Digital inputs
• Internal data processing and logic
• Data on internal drive
• Grid Code application for online audits
• Has GPS synched signals
• Configure/monitor/download via LAN
• Automated reporting with Master Station
https://www.digsilent.de/en/grid-code-compliance-monitoring.html
Level 13, Suite 11, Level 2, Level 5, 82 Eagle Street Umberto Cella
484 St Kilda Rd 189 St Georges Terrace Brisbane Jennifer Crisp
Melbourne VIC 3004 Perth, WA 6000 QLD 4000 Tim George
@digsilent-pacific
[email protected]
digsilent.com.au
Copyright ©️ DIgSILENT Pacific Ptd Ltd 2023. All rights reserved. This document is subject to contract and contains confidential and proprietary information.